This topic relates to lime scale deposits in a cold water roof tank with a hyrofor (pressurised system).
My daughters flat in Nicosia has a roof tank and a hydrofor which provides pressure to the hot and cold water system.
A few months ago the cold water tank was over flowing and i thought it was a problem with the ballcock assembly, which I changed but to no good result.
I continued to check the system and discovered that the one way valve on the cold outlet had pieces of limescale lodged in the valve cause the water from the gound level tank to back fill the tank and thus it overflowed.
I have now cleaned the valves and also changed them on two occaisions since then but it seems that more limescale finds its way into the one way valve lodging it open and thus causing water to flow past the valve into the tank.
All i can think of now is to remove all limescale from the two tanks, which in this weather is more difficult.
Has anyone out there had similar problems? If so how did you rectify the problem.
Is there anything that can be fitted to the tank to stop the deposit of lime / salts. The water is very salty / heavy in lime deposits.
All of the fitting ie check valves etc seem to be suffering from the heavy lime / salts in the water.
Any advise would be much appreciated.
I know a water softener would help but they are expensive.
Problem with lime/salt deposit jamming open one way valve
Moderators: PoshinDevon, Soner, Dragon
-
- Kibkommer
- Posts: 382
- Joined: Tue 03 Apr 2012 3:32 pm
-
- Kibkommer
- Posts: 1013
- Joined: Tue 03 Apr 2012 7:46 pm
Re: Problem with lime/salt deposit jamming open one way valv
An in-line limescale inhibitor will solve the problem but it will take time to dissolve existing scale.
-
- Kibkommer
- Posts: 382
- Joined: Tue 03 Apr 2012 3:32 pm
Re: Problem with lime/salt deposit jamming open one way valv
Thanks TRNCV for your help. Any idea of cost of the unit/ is it ionic or does it work of mains electric. Problem here is the water in Nicosia is so heavily polluted.
Also where can you get one?
Also where can you get one?
-
- Kibkommer
- Posts: 483
- Joined: Mon 23 Jul 2012 12:57 pm
Re: Problem with lime/salt deposit jamming open one way valv
I clean my ground, roof and hot water tanks every couple of years because, even if there isn't a problem like yours, I still get lots of limescale 'grit' blocking tap filters, toilet ballcocks etc.
Now in addition I have put short lengths of pipe (approx. 2 inches) into the outlets on all the tanks. This leaves a 2" deposit area for the limescale grit to collect which vastly reduces the amount that gets into the house system. It still needs cleaning of course but it reduces problems between cleans.
Now in addition I have put short lengths of pipe (approx. 2 inches) into the outlets on all the tanks. This leaves a 2" deposit area for the limescale grit to collect which vastly reduces the amount that gets into the house system. It still needs cleaning of course but it reduces problems between cleans.
-
- Kibkommer
- Posts: 1013
- Joined: Tue 03 Apr 2012 7:46 pm
Re: Problem with lime/salt deposit jamming open one way valv
I can let you have a Scalemaster system which is in-line and requires no electricity. Cost to you, supply only, £149 inc VAT. Fitting is easy for any plumber.philyesil wrote:Thanks TRNCV for your help. Any idea of cost of the unit/ is it ionic or does it work of mains electric. Problem here is the water in Nicosia is so heavily polluted.
Also where can you get one?
-
- Kibkommer
- Posts: 382
- Joined: Tue 03 Apr 2012 3:32 pm
Re: Problem with lime/salt deposit jamming open one way valv
Thanks everyone for their help. I am going to speak to my daughter about the Scalemaster. I will contact you again if she wants to gom ahead.